摘要:本文介绍了安科瑞APM系列交流电表在保加利亚光伏系统交流侧的应用。主要用于光伏系统中的电流的计量,配合互感器对电路系统进行计量、通讯和控制等。
Abstract: This paper introduces the application of ackry APM series AC meter in the AC side of Bulgarian photovoltaic system. It is mainly used to measure the current in the photovoltaic system, and cooperate with the transformers to measure, communicate and control the circuit system.
1.项目概述Project Overview
该公司位于保加利亚,公司主要在保加利亚及周边国家从事小型光伏发电中心项目的设计/安装施工/维护等业务。客户想要使用交流电表APM801、APM810等和互感器,用于光伏系统交流侧电流电压的监测计量、通讯以及利用APM电表的开关量功能进行控制。
The company is located in Bulgaria. The company is mainly engaged in the design / installation, construction / maintenance of small photovoltaic power generation center projects in Bulgaria and surrounding countries. The customer wants to use AC meters apm801, apm810 and mutual inductors for monitoring, metering and communication of current and voltage at the AC side of photovoltaic system, and control by using the switching value function of APM meter.
2.APM系列仪表简介APM Series Energy Meters
APM系列电能表具有全功率测量、电能统计、电能质量分析和网络通信等功能,主要用于供电网络质量的综合监测。
本系列仪表采用模块化设计,具有丰富的外部DI/DO模块、AI/AO模块、带T-Flash(TF)卡的事件记录(SOE)模块、网络通信模块、温湿度测量模块功能,可实现电路全功率测量和开关状态监测,具有以太网接口的双RS485可实现RS485主站的数据拷贝,无需进行数据交换。PROFIBUS-DP接口可实现高速数据传输和联网功能。
APM series power meters of ACREL are power meters that are designed according to IEC standards and synchronized with international advanced technology.
APM series meters have full power measurement, energy statistics, analysis of power quality and network communications and other functions, are mainly used for comprehensive monitoring of the quality of power supply network.
This series of meters use a modular design, with a rich function of the external DI / DO module, AI / AO module, event recording (SOE) module with T-Flash (TF) card, network communication module, Temperature and humidity measurement module, can achieve full power measurement of electrical circuit and monitoring of switch status, Dual RS485 with Ethernet interface can realize data copying of RS485 master station, eliminating the need for data switching exchange. PROFIBUS-DP interface can realize high-speed data transmission and networking function.
3.型号及功能介绍Type and Function Description
Function APM800
(class 0.5s) APM801
(class 0.2s) APM810
(class 0.5s)
Measured parameters Total electrical measurement √ √ √
Four-quadrant energy √ √ √
Pulse output of energy Pulse output of active/reactive energy √ √ √
Demand Three-phase current, active power, reactive power, real-time demand of apparent power, and maximum demand (including time stamp) √ √ √
Extreme value statistics Extremum of current, line voltage, phase voltage, active power, reactive power, apparent power, power factor, frequency, total harmonic of current, total harmonic of voltage in this month and last month (including time stamp) √ √ √
Power quality Unbalance of current, line voltage, phase voltage √ √ √
Voltage phase angle, current phase angle √ √ √
Voltage current phase Angle √ √ √
Total (odd, even) harmonic content of voltage and current × × √
Harmonic content of voltage and current (2-63 times)① × × √
Voltage crest factor × × √
Telephone waveform factor × × √
Current K-factor × × √
Alarm records A total of 66 kinds of alarm types, each type can record the most recent 16 alarm records, support extended records by TF card √ √ √
Event log Record the most recent 128 event records, support extended records by TF card √ √ √
Communication Modbus protocol √ √ √
I/O 2 digital inputs + 2 digital outputs (2DI+2DO) √ √ √
Extensions MD82 8 digital inputs + 2 digital outputs with changeover contacts (8DI+2DO) √ √ √
MLOG TF card storage (alarm records, event records, electrical parameters and energy timing records, etc.) √ √ √
MA84 8 analog inputs (class 0.5) + 4 analog outputs (class 0.5) (8AI+4AO) √ √ √
MCM 1 RS485/Modbus-RTU, support master mode or slave mode √ √ √
MCP 1 Profibus-DP √ √ √
MCE 1 Ethernet, support Modbus-TCP, http, SMTP, DHCP protocol √ √ √
MTH 4 ways of temperature measurement, 1 way of temperature and humidity control √ √ √
4.技术参数Technical parameters
Table 2 technical parameter descriptions
Technical Parameters Index
Signal Electrical network Three-phase three-wire, three-phase four-wire, see the wiring diagram;
Frequency 45~65Hz;
Voltage Rated value:AC 100V、110V、400V、690V;
Overload: 1.2 times rated value(continuous); 2 times rated value /1 second;
Power consumption: < 0.5VA (per channel);
Current Rated value: AC 1A, 5A, support 4 mm2 line access;
Overload: 1.2 times rated value(continuous); 10 times rated value/1 second;
Measurement accuracy Voltage、current and power class 0.5s/class 0.2s (APM800、APM810/APM801)
Active power class 0.5s/class 0.2s (APM800、APM810/APM801)
Reactive power class 2
Harmonic 1%(2rd~42nd)、2%(43rd~63rd)
Switch inputs Dry contact inputs, built-in power supply;
Relay outputs Contact type: open contact in main part, changeover contact in module;
Contact capacity:AC 250V/3A DC 30V/3A;
Pulse output of energy Output mode: Optocoupler pulse with open collector;
Pulse constant:4000(5A)、8000(1A) imp/kWh;
Analog outputs DC 0mA~20mA、4mA~20mA、0V~5V、1V~5V output, accuracy class 0.5%, load resistance ≤ 500Ω;
Analog inputs DC 0mA~20mA、4mA~20mA、0V~5V、1V~5V iutput, accuracy class 0.5%
Storage card Standard Capacity:4G,TF Card Up to 32G Capacity;
Communication RS485 interface/Modbus-RTU protocol and DLT645 protocol
Profibus-DP interface/Profibus-DP protocol;
RJ45 interface (Ethernet) / Modbus-TCP, http, DHCP and other protocols;
Power supply Working range: AC/DC 85V~265V or AC/DC 115~415V(P2);
Power consumption: Power consumption of the main part ≤ 15VA;
Safety Power frequency withstand voltage The power frequency withstand voltage between the shell and the auxiliary power supply, each bbbbb and output terminal group is AC 4kV/1min;
The power frequency withstand voltage between the auxiliary power supply and each bbbbb and each output terminal group is AC 2kV/1min;
The power frequency withstand voltage between the voltage bbbbb and other bbbbb/output terminal groups is AC 2kV/1min;
The power frequency withstand voltage between the current bbbbb and other bbbbb/output terminal groups is AC 2kV/1min;
The power frequency withstand voltage between the relay output and other bbbbb/output terminal groups is AC 2kV/1min;
The power frequency withstand voltage between each terminal group of switch bbbbb, communication, analog output and pulse output is AC 1kV/1min;
Insulation resistance Inputs、outputs to the shell>100MΩ;
Electromagnetic compatibility Meet IEC 61000 standard (Level 4);
Protection level Display panel IP52
Environment Operating temperature: -20 °C ~ +65 °C;
Storage temperature: -20°C~+70°C;
Relative humidity: ≤95% without condensation;
Altitude: ≤2500m;
Standards IEC 60068-2-1
IEC 60068-2-2
IEC 60068-2-30 Environmental Testing-Part 2-1:Tests Test A:Cold IDA
Part 2-1:Tests Test B:Dry heat
Part 2-30:Tests Test Db:Damp heat,cyclic(12+12h)
IEC 61000-4 Electromagnetic compatibility-Testing and measurement techniques
IEC 61557-12 Electrical safety in low voltage distribution system up to 1000V a.c. and1500V d.c –Equipment for testing,measuring or monitoring of protective measures- Part12:
Performances measuring and monitoring devices(PMD)
IEC 62053-22 Electricity metering equipment (a.c.)-Particular requirements - Part22:Static meter for active energy(class 0.2s and 0.5s)
5.客户特殊需求 Requirements from Customer
电网供应商要求:
(1)监控电压:L1-N、L2-N、L3-N。非标称 = 230V
(2)过压时切换继电器输出。分为两步,
第1步:110% 非标称或 253V - 延迟 60 秒(s);
第2步,115% 的非标称或 264V - 延迟 0.1s;设置范围: U:非标称的 100-140%,未列出步骤,可能是 1V 或 1%;延迟0.05s 到 60s,未列出步骤,可能 1s;
(3)欠压时切换继电器输出:
第1步;非标称电压或 184V 的 80% - 延迟 0.2s;设置范围: U:非标称电压的 10-100%,未列出步骤,可能是 1V 或 1%;延迟0.05 s 到 3s,步骤未列出,可能为 1s;
(4)过频时切换继电器输出:
第1步; 50.5Hz——延迟0.1s;设置范围:F:50-52.5Hz,step 0.1Hz;延迟
(5)超频时切换继电器输出
(6)恢复延迟。由于先前的一些原因,当DO打开时,在网格参数回到标称范围后应该有时间延迟。时间范围1-60秒,step 1秒
(7)附加设置。(如果可能的话)。
7.1.当非标称值低于60-70% 时,可禁用低频和超频监测;
7.2. 当发生超频/低频时 -- DO不应该自动恢复,它应该等待手动/远程等方式恢复。
terms of reference from grid supplier:
(1)monitoring voltages: L1-N, L2-N, L3-N. Unominal = 230V;
(2)switching relay output at overvoltage: 2 steps:
Step 1: 110% of Unominal or 253V - delay 60 seconds (s) ;
Step 2: 115% of Unominal or 264V - delay 0.1s;
(3)switching relay output at undervoltage:
1-step; 80% of Unominal or 184V - delay 0.2s; Range of settings: U: 10-100% of Unominal, step not listed, maybe 1V ot 1%; Delay: 0.05 s to 3s, step - not listed, maybe 1s;
(4)switching relay output at overfrequency
1-step; 50.5Hz - delay 0.1s; Range of settings: F: 50-52.5Hz, step 0.1Hz; Delay: 0.1-0.5s, step - maybe 0.1s;
(5)switching relay output at overfrequency
1- step; 47.5Hz - delay 0.1s; Range of settings: F: 47.5-50Hz, step 0.1Hz; Delay: 0.1-0.5s, step - maybe 0.1s;
(6)Delay for recovering. When DO is on by some of previous reasons, there should be time delay after grid parameter(s) are back in nominal range(s). Time range 1-60s, step 1s
(7)Additional settings. (If they are possible).
7.1 When Unominal is lower than 60-70%, under and overfrequency monitoring can be disabled
7.2 When overfrequency/underfrequency is happened - the DO should not be recovered automatically, it should wait for some kind of manual/remote restore.
上述7点为客户对所采购产品的特殊需求,除第七点中部分要求不能满足客户外,其余需求都能满足。基本完好解决了客户的需求。
The above 7 items are the special needs of customers for the purchased products. Except that some requirements in point 7 cannot meet the needs of customers, other needs can be met. Basically solved the needs of customers.
6.安装图片Installation Picture