MTL7060AC 安全栅现货直发
型号:
MTL7060AC
Supply | ||
Connection | terminals 9+, 10- or power feed module/Power Rail | |
Rated voltage | 19 ... 30 V DC | |
Ripple | within the supply tolerance | |
Power dissipation | ≤ 0.98 W | |
Power consumption | max. 0.98 W | |
Interface | ||
Programming interface | programming socket | |
Input | ||
Connection side | field side | |
Connection | terminals 1, 2, 3, 4 | |
RTD | type Pt10, Pt50, Pt100, Pt500, Pt1000 (EN 60751: 1995) type Pt10GOST, Pt50GOST, Pt100GOST, Pt500GOST, Pt1000GOST (6651-94) type Cu10, Cu50, Cu100 (P50353-92) type Ni100 (DIN 43760) | |
Measuring current | approx. 200 µA with RTD | |
Types of measuring | 2-, 3-, 4-wire connection | |
Lead resistance | max. 50 Ω per line | |
Measurement loop monitoring | sensor breakage, sensor short-circuit | |
Thermocouples | type B, E, J, K, N, R, S, T (IEC 584-1: 1995) type L (DIN 43710: 1985) type TXK, TXKH, TXA (P8.585-2001) | |
Cold junction compensation | external and internal | |
Measurement loop monitoring | sensor breakage | |
Potentiometer | 0 ... 20 kΩ (2-wire connection), 0.8 ... 20 kΩ (3-wire connection) | |
Voltage | selectable within the range -100 ... 100 mV | |
Input resistance | ≥ 1 MΩ (-100 ... 100 mV) | |
Output | ||
Connection side | control side | |
Connection | terminal 5: source (-), terminal 6: source (+), terminal 7: sink(-), terminal 8: sink (+) | |
Output | Analog current output | |
Current range | 0 ... 20 mA or 4 ... 20 mA | |
Fault signal | downscale 0 or 2 mA, upscale 21.5 mA (acc. NAMUR NE43) | |
Source | load 0 ... 550 Ω open-circuit voltage ≤ 18 V | |
Sink | Voltage across terminals 5 ... 30 V. If the current is supplied from a source > 16.5 V, series resistance of ≥ (V - 16.5)/0.0215 Ω is needed, where V is the source voltage. The maximum value of the resistance is (V - 5)/0.0215 Ω. |