HICTB16-YC3-RRB-KS-CC-AI16 现货直发
型号:
Supply | ||
Connection | X20: terminals 3, 5(+); 4, 6(-) | |
Nominal voltage | 24 V DC , in consideration of rated voltage of used isolators | |
Voltage drop | 0.9 V , voltage drop across the series diode on the termination board must be considered | |
Ripple | ≤ 10 % | |
Fusing | 4 A , in each case for 16 modules | |
Power dissipation | ≤ 500 mW , without modules | |
Reverse polarity protection | yes | |
Redundancy | ||
Supply | Redundancy available. The supply for the isolators is decoupled, monitored and fused. | |
Fault indication output | ||
Connection | X20: terminals 1, 2 | |
Output type | volt-free contact | |
Switch behaviour | no fault: relay contact closed power supply fault: relay contact open module fault: relay contact open | |
Contact loading | 30 V DC , 1 A | |
Indicators/settings | ||
Display elements | LEDs PWR ON (Termination Board power supply) - LED power supply I, green LED - LED power supply II, green LED LED FAULT (fault indication), red LED - LED lits: module fault - LED flashes: power supply fault | |
Directive conformity | ||
Electromagnetic compatibility | ||
Directive 2014/30/EU | EN 61326-1:2013 (industrial locations) | |
Conformity | ||
Electromagnetic compatibility | NE 21:2017 For further information see system description. | |
Degree of protection | IEC 60529:2001 | |
Ambient conditions | ||
Ambient temperature | -20 ... 60 °C (-4 ... 140 °F) | |
Storage temperature | -40 ... 70 °C (-40 ... 158 °F) | |
Mechanical specifications | ||
Degree of protection | IP20 | |
Connection | ||
Field side | explosion hazardous area: spring terminals , blue | |
Control side | non-explosion hazardous area: Yokogawa system connector, 40-pin | |
Supply | pluggable screw terminals , black | |
Fault output | pluggable screw terminals , black | |
Core cross section | spring terminals: rigid: 0.2 ... 2.5 mm2 flexible: 0.25 ... 1.5 mm2 | |
Material | housing: polycarbonate | |
Mass | approx. 645 g | |
Dimensions | 240 x 175 x 153 mm (9.45 x 6.9 x 6.02 inch) (W x H x D) , depth including module assembly | |
Mounting | on 35 mm DIN mounting rail acc. to EN 60715:2001 | |
Data for application in connection with hazardous areas | ||
EU-type examination certificate | CESI 06 ATEX 022 | |
Marking | ![]() II (1)G [Ex ia Ga] IIC ![]() II (1)D [Ex ia Da] IIIC ![]() I (M1) [Ex ia Ma] I | |
Non-hazardous area | ||
Maximum safe voltage | 250 V (Attention! Um is no rated voltage.) | |
Galvanic isolation | ||
Field circuit/control circuit | safe electrical isolation acc. to IEC/EN 60079-11, voltage peak value 375 V | |
Directive 2014/34/EU | EN IEC 60079-0:2018+AC:2020 , EN 60079-11:2012 , EN 50303:2000 |